Annual testing reveals that a beam smoke detector alarms at the correct attenuation filter, but its alignment is off and it reports trouble every few days. What is the right action?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2044
- D: Realign it per the manufacturer and confirm it is mounted on a stable surface
Explanation
Projected beam detectors are sensitive to alignment and to movement of the surfaces they are mounted on. Intermittent trouble often comes from building movement or a loose mount, and the fix is solid mounting and realignment per the manufacturer.