Question 3019 of 243 · NICET Fire Alarm Systems Level IV
Why does a voice system need 15 minutes of alarm capacity on secondary power while a horn and strobe system needs only 5 minutes?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3019
- D: Voice systems support staged evacuation and responder announcements that run longer
Explanation
EVACS may be used for relocation, phased evacuation and live fire service announcements that last well beyond a quick evacuation. The code therefore requires 15 minutes of alarm at maximum connected load after the standby period, compared with 5 minutes for other systems.
More questions: Complex Notification and Emergency Communication Systems