Question 3019 of 243 · NICET Fire Alarm Systems Level IV

Why does a voice system need 15 minutes of alarm capacity on secondary power while a horn and strobe system needs only 5 minutes?

Exactly one answer is correct.

Show solution

Correct answer to question 3019

  • D: Voice systems support staged evacuation and responder announcements that run longer

Explanation

EVACS may be used for relocation, phased evacuation and live fire service announcements that last well beyond a quick evacuation. The code therefore requires 15 minutes of alarm at maximum connected load after the standby period, compared with 5 minutes for other systems.