What distinguishes pathway survivability Level 3 from Level 2?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3042
- C: Level 3 also requires the building to be fully sprinklered
Explanation
Level 2 uses 2-hour rated cable, a 2-hour rated enclosure or a protected area. Level 3 adds the requirement that the building be fully sprinklered.