What minimum size does the IBC set for a high-rise fire command center?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4037
- B: 200 sq ft, with no dimension under 10 ft
Explanation
The fire command center must be at least 200 sq ft with a minimum dimension of 10 ft. This space holds the EVACS, FSCS, phone system and other controls used by fire fighters.