Question 1024 of 183 · Ohio Fire Alarm Certification Exam
Fire alarm devices are inaccessible for safety reasons during normal operations. What testing interval does the Ohio Fire Code allow?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1024
- D: Testing during approved scheduled shutdowns, at least every 18 months
Explanation
OFC 907.8.2 normally requires testing per the NFPA 72 schedules. Its exception lets inaccessible devices be tested during scheduled shutdowns where approved, but not less than every 18 months.