Question 2007 of 183 · Ohio Fire Alarm Certification Exam
Before testing a monitored fire alarm system, whom should the technician notify?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2007
- A: The building occupants and the supervising station
Explanation
NFPA 72 requires notice to occupants and to the supervising station (and other parties receiving signals) before testing so that test signals do not cause an unwanted response. They are notified again when testing is complete.
More questions: Fundamentals, Definitions and Documentation
- 2008A required fire alarm system will be impaired for more than how long in a 24 hour period before the AHJ must be notified and mitigation such as a fire watch provided?
- 2009When fire alarm record documents are kept in a cabinet, how must the cabinet be labeled?
- 2010In NFPA 72, what does the term approved mean?
- 2011In NFPA 72, what is the authority having jurisdiction (AHJ)?
- 2012What does the term listed mean in NFPA 72?
- 2013In NFPA 72, what is the difference between shall and should?