How must the outgoing and return conductors of a Class A circuit generally be routed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4024
- A: Separately, so a single event cannot damage both
Explanation
The value of Class A is the redundant path. NFPA 72 requires outgoing and return conductors to be routed separately, with limited exceptions such as short drops to a single device or within an enclosure.