How must the outgoing and return conductors of a Class A circuit generally be routed?

Exactly one answer is correct.

Show solution

Correct answer to question 4024

  • A: Separately, so a single event cannot damage both

Explanation

The value of Class A is the redundant path. NFPA 72 requires outgoing and return conductors to be routed separately, with limited exceptions such as short drops to a single device or within an enclosure.