Question 3002 of 243 · NICET Fire Alarm Systems Level IV
For an EVACS in a high-rise office building, which group of paging zones does the IBC require as a minimum?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3002
- A: Each floor, interior exit stairways, elevator groups and areas of refuge
Explanation
The IBC requires speakers throughout the building arranged in paging zones, at minimum one for each elevator group, each interior exit stairway, each floor and each area of refuge. This lets the fire service give different instructions to different parts of the building.