Question 3001 of 243 · NICET Fire Alarm Systems Level IV
A new Group A assembly building will have an occupant load of 1,200. Which occupant notification method does the IBC require for it?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3001
- D: An emergency voice/alarm communication system
Explanation
The IBC requires an emergency voice/alarm communication system in Group A occupancies with an occupant load of 1,000 or more. Below that threshold, standard audible and visible notification is generally acceptable.
More questions: Complex Notification and Emergency Communication Systems
- 3002For an EVACS in a high-rise office building, which group of paging zones does the IBC require as a minimum?
- 3003Which manual control does the IBC require at an EVACS control unit?
- 3004In an ECS, a live voice announcement starts while a prerecorded evacuation message is playing in the same zone. What should happen?
- 3005What is the standard audible evacuation signal for total evacuation when no voice message is used?
- 3006A voice evacuation message is designed around an alert tone. How is the tone typically arranged with respect to the message?
- 3007Under the public mode audibility rule, what minimum sound level is required in a space with an average ambient level of 68 dBA and no loud sounds lasting 60 s or more?