Question 3016 of 243 · NICET Fire Alarm Systems Level IV
A zone has 64 speakers tapped at 1 W and 20 speakers tapped at 2 W. The design adds 20 percent spare capacity. What minimum amplifier rating is needed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3016
- C: 125 W
Explanation
Connected load is 64 x 1 W + 20 x 2 W = 104 W. Adding 20 percent spare gives 104 x 1.2 = 124.8 W, so a 125 W amplifier or larger is needed.
More questions: Complex Notification and Emergency Communication Systems
- 3017A 70.7 V speaker circuit carries a total speaker load of 50 W. What current does the circuit draw?
- 3018An EVACS draws 3 A in standby and 14 A in alarm. Before any safety factor, what battery capacity is needed?
- 3019Why does a voice system need 15 minutes of alarm capacity on secondary power while a horn and strobe system needs only 5 minutes?
- 3020What is the recommended acceptance criterion for intelligibility when measured with the STI method?
- 3021What is an acoustically distinguishable space (ADS)?
- 3022During design of a voice system for a parking garage, the engineer marks the garage as an ADS where intelligibility is not required. What must still be achieved there?