Question 3029 of 243 · NICET Fire Alarm Systems Level IV
Three strobes are visible from one point in an open office. What requirement applies to them?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3029
- B: Their flashes must be synchronized
Explanation
Where more than two visible appliances are in any field of view, their flashes must be synchronized. Unsynchronized flashes create a combined flash rate that can trigger photosensitive seizures.
More questions: Complex Notification and Emergency Communication Systems
- 3030A corridor 12 ft wide and 210 ft long needs visible notification. What spacing rule applies to the strobes?
- 3031What flash rate range applies to visible notification appliances?
- 3032A campus requests mass notification strobes for non-fire emergencies. What color guidance applies?
- 3033What is the basis for deciding whether a building needs mass notification and how it must perform?
- 3034A university risk analysis shows that an active shooter message should take precedence over a fire evacuation signal. What does the code allow?
- 3035Which system type uses text messages, email and phone calls to reach specific people?