In a hotel sleeping room, the strobe will be mounted 18 in. below the ceiling. What minimum effective intensity is required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3028
- B: 177 cd
Explanation
Sleeping area visible appliances must be 110 cd when mounted more than 24 in. below the ceiling, and 177 cd when within 24 in. of the ceiling, where smoke collects first. At 18 in. below the ceiling, 177 cd is required.