Question 3040 of 243 · NICET Fire Alarm Systems Level IV
For an in-building MNS, what secondary power duration is generally required where the system is used for emergencies?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3040
- A: 24 h of standby followed by 15 minutes of alarm
Explanation
Secondary power for in-building emergency voice and mass notification service follows the voice system rule: 24 hours of quiescent load followed by 15 minutes of operation at maximum connected load. A risk analysis can require a longer duration, but it never drops to zero.
More questions: Complex Notification and Emergency Communication Systems