Under NFPA 92, how often must a dedicated smoke control system be operationally tested?

Exactly one answer is correct.

Show solution

Correct answer to question 4017

  • C: Semiannually

Explanation

NFPA 92 requires dedicated smoke control systems to be tested semiannually and nondedicated systems annually. The tests verify each operating mode under all available power sources.