A duct smoke detector is connected to a building fire alarm system. What signal does its activation normally initiate?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4035
- C: A supervisory signal, unless an alarm signal is required
Explanation
Where duct detectors are connected to a fire alarm system, activation is normally indicated as a supervisory signal, unless other codes or the AHJ require an alarm. Confirm the exact provision in the edition and in NFPA 90A.