Question 2003 of 183 · Ohio Fire Alarm Certification Exam
A sprinkler control valve on a monitored system is partly closed. Which signal should the fire alarm system produce?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2003
- B: A supervisory signal
Explanation
A supervisory signal reports an off normal condition of a monitored suppression system, such as a valve moved from its normal position. Trouble signals report faults in the fire alarm system itself.