In an elevator machine room with sprinklers, heat detectors used to shut down elevator power must be placed where?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4015
- B: Within 2 feet of each sprinkler head
Explanation
For elevator shutdown before sprinkler discharge, NFPA 72 requires a heat detector within 2 ft of each sprinkler, with a lower temperature rating and higher sensitivity than the sprinkler.