Question 4015 of 183 · Ohio Fire Alarm Certification Exam

In an elevator machine room with sprinklers, heat detectors used to shut down elevator power must be placed where?

Exactly one answer is correct.

Show solution

Correct answer to question 4015

  • B: Within 2 feet of each sprinkler head

Explanation

For elevator shutdown before sprinkler discharge, NFPA 72 requires a heat detector within 2 ft of each sprinkler, with a lower temperature rating and higher sensitivity than the sprinkler.