Question 4016 of 183 · Ohio Fire Alarm Certification Exam
How close may a spot type smoke detector be to an air supply diffuser?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4016
- B: No closer than 36 inches
Explanation
NFPA 72 keeps spot type smoke detectors out of direct airflow and at least 36 in from air supply diffusers and return air openings, because moving air can blow smoke away from the detector.