What is the standard audible evacuation signal pattern required by NFPA 72?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5006
- C: Three pulse temporal pattern
Explanation
NFPA 72 requires the three pulse temporal pattern (ANSI/ASA S3.41) for evacuation: three half second on pulses separated by half second off periods, then a 1.5 second pause. The four pulse pattern is used for carbon monoxide.