When must visible notification appliances in a room be synchronized?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5008
- B: When more than two are in any field of view
Explanation
NFPA 72 requires synchronization where more than two visible appliances are in any field of view, to reduce the risk of photosensitive seizures.
More questions: Notification Appliances
- 5009What flash rate must visible notification appliances have?
- 5010A horn produces 90 dBA at 10 feet. About what level can be expected at 20 feet in free field conditions?
- 5011Two horns each produce 80 dBA at a point. About what is the combined sound level there?
- 5012In a sleeping room, a visible appliance is mounted within 24 inches of the ceiling. What minimum effective intensity is required?
- 5013Using the room spacing table, what minimum strobe intensity is needed for one wall mounted strobe in a 30 by 30 foot room?
- 5014Using the room spacing table, what minimum strobe intensity is needed for one wall mounted strobe in a 40 by 40 foot room?