Using the room spacing table, what minimum strobe intensity is needed for one wall mounted strobe in a 40 by 40 foot room?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5014
- A: 60 candela
Explanation
For a 40 by 40 ft room the NFPA 72 table calls for 60 cd with a single wall mounted appliance. Larger rooms need higher intensity or more appliances.