Question 5019 of 183 · Ohio Fire Alarm Certification Exam
At what height above the floor is audible signal sound pressure normally measured?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5019
- D: 5 feet
Explanation
NFPA 72 calls for sound pressure levels to be measured 5 ft above the floor unless otherwise specified, roughly at the height of a standing person's ear.
More questions: Notification Appliances
- 5020A horn produces 96 dBA at 10 feet. About what level can be expected at 40 feet in free field conditions?
- 5021How long does one complete cycle of the three pulse temporal pattern take?
- 5022Which audible pattern is used for carbon monoxide alarm signals?
- 5023What light color must visible notification appliances used for fire alarm signaling have?
- 5024In a sleeping room, how far from the pillow may the visible notification appliance be?
- 5001In public mode, how far above the average ambient sound level must audible alarm signals be?