In a sleeping room, how far from the pillow may the visible notification appliance be?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5024
- C: Within 16 feet
Explanation
NFPA 72 requires the visible appliance in a sleeping area to be within 16 ft of the pillow, in addition to the 177 cd or 110 cd intensity rule based on mounting height.
More questions: Notification Appliances
- 5001In public mode, how far above the average ambient sound level must audible alarm signals be?
- 5002What maximum sound pressure level must audible notification not exceed at the minimum hearing distance?
- 5003In private mode, how far above the average ambient sound level must audible signals be?
- 5004What is the minimum audible signal level at the pillow in a sleeping area, when no higher value results from the ambient sound?
- 5005Which audible signal is required to wake occupants in sleeping rooms of Group R-1 and R-2 when a fire alarm system is required?
- 5006What is the standard audible evacuation signal pattern required by NFPA 72?