A defect found during inspection is not corrected by the end of the visit. What should the technician do?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6019
- A: Notify the owner or designated representative in writing
Explanation
NFPA 72 requires system defects to be corrected. If they are not fixed during the visit, the owner or designated representative must be informed in writing so the impairment can be managed.