Question 6025 of 183 · Ohio Fire Alarm Certification Exam
During the annual test of secondary power, what is done?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6025
- A: Primary power is disconnected and the system is checked on batteries
Explanation
The test proves that the system transfers to secondary power and operates normally on it, including trouble indication for the loss of primary power.
More questions: Inspection, Testing and Maintenance
- 6026A building has 300 non restorable spot type heat detectors that are 15 years old. How many must go to a lab if the owner does not replace them all?
- 6027What is a visual inspection of fire alarm devices meant to find?
- 6028When must valve regulated lead acid (VRLA) batteries in a fire alarm system be replaced at the latest?
- 6001How often must spot type smoke detectors be functionally tested under NFPA 72?
- 6002When must the first sensitivity test of a smoke detector be performed after installation?
- 6003After the second required sensitivity test, a detector has stayed within its listed range. To what maximum may the interval be extended?