Question 2001 of 153 · Oklahoma Fire Alarm Technician Exam
A system draws 0.4 A in standby and 2.4 A in alarm. Ignoring any safety margin, what battery capacity is needed for 24 hours standby plus 5 minutes alarm?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2001
- D: 9.8 Ah
Explanation
Standby: 0.4 A x 24 h = 9.6 Ah. Alarm: 2.4 A x (5/60) h = 0.2 Ah. Total 9.6 + 0.2 = 9.8 Ah. Multiplying the alarm current by 24 hours is the classic error.
More questions: Basic Electronics and Calculations
- 2002Standby load is 0.25 A and alarm load is 3.0 A. Under NFPA 72 (2016) the designer applies the 20 percent safety margin, with 24 hours standby and 5 minutes alarm. What is the minimum battery size?
- 2003A notification appliance circuit carries 1.5 A. Each conductor is 250 ft long and the wire resistance is 2.0 ohms per 1,000 ft. What is the voltage drop on the circuit?
- 2004An initiating device circuit has a 24 V supply and a 4,700 ohm end of line resistor. Ignoring wire resistance, what supervisory current flows?
- 2005A technician finds a ground fault trouble on the panel. What is the most likely cause?
- 2006A 24 VDC notification circuit draws 2.5 A. What power does it consume?
- 2007Resistors of 100, 220 and 330 ohms are connected in series. What is the total resistance?