Question 2002 of 153 · Oklahoma Fire Alarm Technician Exam

Standby load is 0.25 A and alarm load is 3.0 A. Under NFPA 72 (2016) the designer applies the 20 percent safety margin, with 24 hours standby and 5 minutes alarm. What is the minimum battery size?

Exactly one answer is correct.

Show solution

Correct answer to question 2002

  • B: 7.5 Ah

Explanation

Standby 0.25 x 24 = 6.0 Ah. Alarm 3.0 x 5/60 = 0.25 Ah. Subtotal 6.25 Ah. With the 20 percent margin: 6.25 x 1.2 = 7.5 Ah. The 2022 edition replaced this margin with a 1.25 aging factor.