Fire alarm cable passes through a 1 hour fire rated wall. What must be done with the opening?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4020
- A: Firestop it with an approved method
Explanation
Penetrations of fire resistance rated walls, floors and ceilings must be firestopped with approved methods so the rating is maintained.