An installer strips too much insulation, leaving bare copper outside a detector terminal. What is the risk?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1083
- C: A short or ground fault if the bare wire touches the box
Explanation
Exposed copper outside the terminal can touch the metal box, a neighboring conductor or the device plate. Strip only the length shown by the manufacturer.
More questions: Installation (Peripherals, Cabling, Job Site Safety)
- 1084A 24 V DC circuit has a 2,400 ohm resistance. What current flows?
- 1085A strobe draws 0.115 A at 24 V. How much power does it use?
- 1086Three resistors of 100 ohm, 220 ohm and 680 ohm are connected in series. What is the total resistance?
- 1087Two 10,000 ohm resistors are connected in parallel. What is the combined resistance?
- 1088A notification appliance circuit carries 1.5 A over a 300 ft one-way run of 14 AWG solid copper with 3.07 ohm per 1,000 ft. What is the voltage drop?
- 1089A 24 V NAC has a calculated voltage drop of 2.76 V. What percentage of the source voltage is that?