NICET Fire Alarm Systems Level I, Installation (Peripherals, Cabling, Job Site Safety): all 147 questions
All questions from the Installation (Peripherals, Cabling, Job Site Safety) section for NICET Fire Alarm Systems Level I, each with the correct answer.
- 1001A spot-type smoke detector has to be mounted on a sidewall instead of the ceiling. Where must the top of the detector be located?
- 1002A spot-type heat detector is being mounted on a smooth ceiling. What is the minimum distance from the sidewall?
- 1003A heat detector must be mounted on a sidewall. Which mounting position meets NFPA 72?
- 1004On a smooth, flat ceiling with no performance-based design, what nominal spacing is used for spot-type smoke detectors?
- 1005Smoke detectors on a smooth ceiling are laid out at a 30 ft nominal spacing. Every point on the ceiling must be within what distance of a detector?
- 1006A heat detector has a listed spacing of 50 ft and is installed on a smooth 9 ft ceiling. What is the maximum distance from any wall to the nearest detector, measured at right angles?
- 1007A heat detector listed for 50 ft spacing is installed on a smooth 15 ft high ceiling. Using the NFPA 72 high ceiling reduction factor of 0.77 for 14 to 16 ft, what is the adjusted spacing?
- 1008The highest expected ceiling temperature in a mechanical room is 120 F. What is the lowest fixed-temperature heat detector rating that may be used?
- 1009A fixed-temperature heat detector is rated 194 F. In which NFPA 72 temperature classification does it fall?
- 1010What color marking identifies a heat detector in the intermediate temperature classification?
- 1011The general contractor asks you to install the smoke detectors while drywall sanding is still going on, and nobody has required detection for protection during construction. What should you do?
- 1012Smoke detectors were installed early to protect a building during construction. What must happen to them before the system is accepted?
- 1013After installing a new smoke detector you notice the plastic dust cover is still on it. When must the cover come off?
- 1014Under which ambient condition may a spot-type smoke detector NOT be installed unless it is specifically listed for that condition?
- 1015A smoke detector is planned for an unheated garage where winter temperatures fall to 20 F. What is the correct approach?
- 1016When mounting a duct smoke detector housing, how must the sampling tube be installed?
- 1017An owner wants to save money by counting the duct smoke detectors as the smoke detection for the open office areas. Is that acceptable?
- 1018At what height must the operable part of a manual fire alarm box be mounted?
- 1019A manual fire alarm box is required at an exit door. Within what distance of the exit doorway opening must it be located?
- 1020On one floor of a building, what is the maximum travel distance from any point to the nearest manual fire alarm box?
- 1021A tenant wants to hide a manual fire alarm box behind a decorative curtain. What does NFPA 72 require?
- 1022A wall-mounted visible notification appliance (strobe) is being hung in a room with a 10 ft ceiling. Where must its lens be?
- 1023A room has a ceiling only 84 in. high, so a wall strobe cannot meet the normal 80 to 96 in. range. Where may it be mounted?
- 1024A wall-mounted horn (audible only) is installed in a room with a 12 ft ceiling. Where must the top of the horn be?
- 1025You are mounting a combination horn/strobe on a wall. Which mounting rule controls its height?
- 1026The drawings show ceiling-mounted strobes, but the installer looks up the candela rating in the wall-mounted spacing table. What is wrong?
- 1027A 40 ft x 40 ft room will be covered by one wall-mounted strobe. Using the NFPA 72 room spacing table, what is the minimum effective intensity?
- 1028A single wall-mounted strobe will cover a 20 ft x 20 ft office. What is the minimum effective intensity from the room spacing table?
- 1029Strobes are being installed in a corridor 10 ft wide and 150 ft long. Which layout meets the corridor rule of the 2022 edition?
- 1030What flash rate must a visible notification appliance used for fire alarm have?
- 1031When must strobes within a field of view be synchronized?
- 1032What light color is required for public mode visible alarm appliances that signal a fire alarm?
- 1033Why must polarity be observed when terminating a horn/strobe on a notification appliance circuit?
- 1034On a conventional Class B initiating device circuit, how should the installer connect the wires at a smoke detector base?
- 1035Where is the end-of-line resistor normally installed on a conventional Class B initiating device circuit?
- 1036Why is a T-tap not allowed on a conventional Class B initiating device circuit that uses an end-of-line resistor?
- 1037What does a Class A pathway provide that a Class B pathway does not?
- 1038A single open occurs halfway along a Class B initiating device circuit. What happens?
- 1039When installing a Class A circuit, how should the outgoing and return conductors be run?
- 1040Which pathway class keeps operating through a single open, a single ground fault, or a single short circuit?
- 1041A single ground fault occurs on a supervised initiating device circuit. What should the panel do?
- 1042Within how many seconds must a single open or single ground fault on monitored installation conductors be indicated?
- 1043On a conventional two-wire smoke detector zone, what is the purpose of the detector base wiring when the head is removed?
- 1044Four-wire smoke detectors get their operating power from a separate power circuit. What must be installed to supervise that power?
- 1045A two-wire smoke detector from a different manufacturer is offered as a replacement on an existing conventional zone. What must be confirmed?
- 1046When installing a fire alarm device, which instructions must be followed in addition to the code?
- 1047Two addressable smoke detectors on the same signaling line circuit were accidentally set to the same address. What is the likely result?
- 1048When installing a vane-type waterflow switch on a sprinkler pipe, what must the installer check?
- 1049A waterflow switch has an adjustable retard. Within what time after water flow begins must the switch activate?
- 1050When must a valve supervisory (tamper) switch send its off-normal signal?
- 1051A ceiling is peaked, with slopes rising to a ridge. Where is the first row of spot-type smoke detectors placed?
- 1052Which article of the National Electrical Code covers fire alarm system wiring?
- 1053A power-limited fire alarm cable will be run through a ceiling space used for environmental air (a plenum). Which cable type is required?
- 1054A power-limited fire alarm cable runs vertically through a shaft from floor to floor. Which cable type is the minimum rating suitable for this riser?
- 1055Your shop has no FPLR on the truck. Which cable may be substituted for FPLR in a riser application?
- 1056Which cable may be used in place of FPLP in a plenum?
- 1057What does the letter group NPLF on a fire alarm cable jacket indicate?
- 1058How does the NEC require fire alarm circuits to be identified?
- 1059Where must equipment supplying power-limited fire alarm circuits be marked as such?
- 1060May a power-limited fire alarm cable be pulled into the same raceway as 120 V lighting conductors?
- 1061An exposed PLFA cable is run near open power and lighting conductors. What minimum separation does the NEC require in other applications?
- 1062How must exposed fire alarm cables be installed according to the NEC?
- 1063May fire alarm cables be supported by the hanger wires of a suspended ceiling grid?
- 1064A fire alarm cable passes through a fire-rated wall. What must be done at the penetration?
- 1065During a renovation you find old fire alarm cable that is no longer connected and not tagged for future use. What does the NEC require?
- 1066Cable is installed through bored holes in wood studs. If the hole is closer than the required distance to the face of the stud, what protection is required?
- 1067What is the minimum size for single conductors used in non-power-limited fire alarm circuits?
- 1068A fire alarm cable must be installed in an underground conduit between two buildings. What must the cable be rated for?
- 1069The branch circuit that supplies a fire alarm control unit must be which of the following?
- 1070How must the disconnecting means of the fire alarm branch circuit be marked?
- 1071Where must the location of the fire alarm branch circuit overcurrent device be recorded?
- 1072May the branch circuit for a fire alarm control unit be protected by a ground-fault circuit interrupter (GFCI)?
- 1073More than two conductors are pulled into a conduit. What maximum percentage of the conduit cross section may they fill?
- 1074Between pull points, what is the maximum total of bends allowed in an EMT run?
- 1075How must EMT be supported near a junction box?
- 1076Cable ties used to bundle fire alarm cables in a plenum must have which property?
- 1077Where must splices in fire alarm wiring be made?
- 1078A shielded cable is used for an addressable loop. Where is the drain wire usually connected?
- 1079When pulling fire alarm cable, what should the installer watch to avoid damaging it?
- 1080In the NEC color code, which insulation color identifies an equipment grounding conductor?
- 1081Which cable type is used where a fire alarm circuit must survive fire for a rated time without extra protection?
- 1082What does pathway survivability Level 0 mean in NFPA 72?
- 1083An installer strips too much insulation, leaving bare copper outside a detector terminal. What is the risk?
- 1084A 24 V DC circuit has a 2,400 ohm resistance. What current flows?
- 1085A strobe draws 0.115 A at 24 V. How much power does it use?
- 1086Three resistors of 100 ohm, 220 ohm and 680 ohm are connected in series. What is the total resistance?
- 1087Two 10,000 ohm resistors are connected in parallel. What is the combined resistance?
- 1088A notification appliance circuit carries 1.5 A over a 300 ft one-way run of 14 AWG solid copper with 3.07 ohm per 1,000 ft. What is the voltage drop?
- 1089A 24 V NAC has a calculated voltage drop of 2.76 V. What percentage of the source voltage is that?
- 1090Using the formula VD = 2 x K x I x L / CM with K = 12.9, find the voltage drop for 1.2 A over 250 ft one way on 14 AWG (4,110 circular mils).
- 1091What is the circular mil area of a 14 AWG conductor?
- 1092Which conductor has the largest cross section?
- 1093A NAC power supply circuit is rated 2.5 A. Each strobe draws 0.12 A. How many strobes can be connected without exceeding the rating?
- 1094Two 12 V, 7 Ah batteries are connected in series for a 24 V panel. What is the result?
- 1095A 24 V NAC can tolerate a maximum voltage drop of 3 V. Total load is 2 A on 14 AWG wire with 3.07 ohm per 1,000 ft. What is the maximum one-way circuit length?
- 1096A 24 V circuit carries 0.5 A. What resistance does the load have?
- 1097What type of power does a typical fire alarm control unit use for its primary supply and for its notification circuits?
- 1098You set up an extension ladder to reach a mezzanine landing. How far must the side rails extend above the upper landing surface?
- 1099At what angle should a non-self-supporting extension ladder be set up?
- 1100An extension ladder has a working length of 20 ft to the top support point. How far from the wall should the base be?
- 1101You need to reach a ceiling detector from a stepladder. Which practice is NOT allowed?
- 1102You must work near exposed energized electrical equipment from a ladder. What type of ladder is required?
- 1103A self-supporting portable ladder must be able to support at least how many times its maximum intended load?
- 1104You find a ladder with a cracked side rail on the job. What must be done?
- 1105A ladder must be set up in a busy hallway next to a door. What is the correct precaution?
- 1106How should you climb up or down a ladder?
- 1107Before using a portable ladder on a construction site, who must inspect it for visible defects?
- 1108On a construction site, at what height does OSHA require fall protection for a worker on an unprotected side or edge?
- 1109A technician does service work in an existing occupied building (general industry). At what height does OSHA require fall protection on an unprotected edge?
- 1110At what height does OSHA require fall protection for workers on a supported scaffold?
- 1111You are working from a boom-supported aerial lift to install a beam detector. What fall protection is required?
- 1112What is the top rail height of a standard guardrail system on a construction site?
- 1113What is the purpose of the OSHA lockout/tagout standard?
- 1114Three technicians will work on the same de-energized equipment. How should lockout be handled?
- 1115Who may remove a lockout device under normal conditions?
- 1116How does a tagout device differ from a lockout device?
- 1117Before touching conductors you have de-energized, you test them with a voltage tester. What else must you do?
- 1118You need to replace a power supply board inside a fire alarm control unit. What must be disconnected to make the unit safe?
- 1119On a construction site, which receptacles used by employees require ground-fault circuit interrupter protection?
- 1120You are drilling overhead into a concrete ceiling to mount a device box. What eye protection is required?
- 1121Drilling into concrete creates dust that contains respirable crystalline silica. Which control method is typical under the OSHA silica standard?
- 1122While pulling cable above a ceiling, you find old sprayed-on fireproofing that may contain asbestos. What should you do?
- 1123Where can a worker find the hazards, PPE and first aid measures for a chemical such as firestop sealant?
- 1124What is the OSHA occupational noise action level, at which a hearing conservation program is required?
- 1125Who is responsible for assessing the workplace for hazards that require personal protective equipment?
- 1126When must workers wear protective helmets (hard hats) on a construction site?
- 1127A coworker has received an electric shock and is still touching the energized conductor. What is the first thing to do?
- 1128Unqualified workers and their conductive tools must stay how far from overhead power lines of 50 kV or less?
- 1129When handling and installing lead-acid standby batteries, which hazard is most important to control?
- 1130Cords and tools are left lying across a stairway at the job site. Which OSHA requirement does this violate?
- 1131A power tool's cord has damaged outer insulation with the inner conductors showing. What should you do?
- 1132On the job you are asked to open a 480 V electrical panel to find a circuit for the fire alarm. You are not trained or qualified for that work. What should you do?
- 1133When a ladder is used to access a ceiling device, where should the ladder be placed?
- 1134Speaker wiring for a voice evacuation system is being installed. A speaker is set to the 1 W tap on a 25 V circuit. Why is the tap setting important?
- 1135An installer mounts a smoke detector directly in the airflow of an HVAC supply diffuser. What is the likely problem?
- 1136In a dwelling unit, a smoke alarm is planned right next to a bathroom door. What minimum horizontal distance from a door to a bathroom with a shower or tub is required, where possible?
- 1137In a dwelling unit with a ceiling fan, how far from the tip of the fan blade must a smoke alarm be located, where possible?
- 1138A new ionization smoke alarm without an alarm silencing feature is planned in a home near the kitchen range. What does NFPA 72 say about this location?
- 1139A detector back box must be mounted on a drop ceiling tile. What is the correct method?
- 1140How many conductors may share a device box is determined by which NEC rule?
- 1141An addressable monitor module will supervise a sprinkler tamper switch. What is the module's job?
- 1142Which device is used to let the fire alarm system switch an external load, such as releasing door holders?
- 1143Where must a relay or control module that performs an emergency control function, such as fan shutdown, be located?
- 1144A sprinkler system serves an elevator machine room and the elevator power is shunt tripped on waterflow. Where must the heat detectors for elevator shutdown be located?
- 1145When a technician mounts a smoke detector near a ceiling beam on a ceiling with deep beams, what must be checked before installation?
- 1146Which NFPA 72 pathway class is intended for Ethernet-type networks with redundant equipment paths?
- 1147An installer mounts a monitor module above a ceiling to watch a sprinkler tamper switch. What should be done so it can be found later?