A 24 V NAC can tolerate a maximum voltage drop of 3 V. Total load is 2 A on 14 AWG wire with 3.07 ohm per 1,000 ft. What is the maximum one-way circuit length?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1095
- B: About 244 ft
Explanation
Maximum loop resistance = 3 V / 2 A = 1.5 ohm. Total wire length = 1.5 / 3.07 x 1,000 = 489 ft, which is out and back, so the one-way length is about 244 ft.