Question 1119 of 299 · NICET Fire Alarm Systems Level I

On a construction site, which receptacles used by employees require ground-fault circuit interrupter protection?

Exactly one answer is correct.

Show solution

Correct answer to question 1119

  • B: 125 V, single phase, 15, 20 and 30 A receptacles not part of permanent wiring

Explanation

OSHA construction rules require GFCI protection (or an assured equipment grounding conductor program) for 120 V, single phase, 15, 20 and 30 A temporary receptacles used by employees.

Next to question ›