Where is a duct smoke detector placed on the supply side of an air handling system under NFPA 90A?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1064
- C: Downstream of filters, ahead of branch connections
Explanation
On the supply side, the detector goes downstream of filters (so it sees smoke from a filter fire) and ahead of branch connections (so it sees all the air). NFPA 72 then governs the detector installation itself.