A grouped opening of exit doors is 60 ft wide. Where are manual fire alarm boxes required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1068
- C: On both sides, within 5 ft of each side
Explanation
Where grouped openings exceed 40 ft (12.2 m) in width, manual boxes are needed on both sides of the grouped opening within 5 ft of each side.