NICET Fire Alarm Systems Level II: all 344 questions with answers
Each question leads to its own page with the answers and the solution.
- Installation118 questions
- Maintenance101 questions
- Submittal Preparation and System Layout90 questions
- Management and Supervision35 questions
Installation
- 1001Which pathway class includes a redundant path and keeps operating past a single open, but is not required to keep operating past a single short?
- 1002A technician opens one conductor in the middle of a Class B initiating device circuit. What happens to the devices beyond the break?
- 1003Which pathway class is designed to keep operating during a single short circuit on the pathway?
- 1004A door holder circuit releases the doors whenever its pathway fails, and no trouble is annunciated. Which pathway class describes this behavior?
- 1005Which pathway class applies to pathways that are not monitored for integrity at all?
- 1006An IP based link to a remote annunciator is checked only through periodic end to end communication, and loss of that communication is reported as trouble. The individual paths are not monitored. Which class is this?
- 1007Which pathway class was created specifically for modern Ethernet infrastructure serving fire alarm or emergency communication devices?
- 1008On a Class A or Class B pathway, how must a single ground fault be treated?
- 1009For a Class A circuit, why does NFPA 72 require the outgoing and return conductors to be routed separately?
- 1010Under the separation rule for Class A and Class X pathways, what minimum separation applies between outgoing and return pathways run vertically?
- 1011Under the separation rule for Class A and Class X pathways, what minimum separation applies between outgoing and return pathways run horizontally?
- 1012What does pathway survivability Level 0 require?
- 1013A pathway is run in metal raceway in a building fully protected by an NFPA 13 sprinkler system. Which survivability level does this describe?
- 1014Which method meets pathway survivability Level 2?
- 1015What distinguishes survivability Level 3 from Level 2?
- 1016Under NFPA 70 Article 760, what are the three types of listed power-limited fire alarm cable, from most to least fire resistive in application?
- 1017A PLFA cable will be installed in a ceiling space used for environmental air (plenum). Which cable type is suitable without a raceway?
- 1018A PLFA circuit runs vertically through floors in a shaft. Which cable type is the lowest rating suitable for that riser application?
- 1019Which cable may be substituted for FPL in a general purpose PLFA application?
- 1020What minimum separation does NFPA 70 generally require between PLFA conductors and electric light or power conductors when neither is in a raceway or a permitted cable sheath?
- 1021May PLFA conductors and 120 V power conductors share the same raceway?
- 1022Which circuit types may share a cable with PLFA conductors under NFPA 70?
- 1023What does NFPA 70 require for the branch circuit supplying a fire alarm control unit?
- 1024Where must the location of the fire alarm branch circuit disconnecting means be documented?
- 1025NFPA 70 requires fire alarm circuits to be identified at terminal and junction locations. What is the purpose?
- 1026How must exposed fire alarm cables above a suspended ceiling be supported under NFPA 70?
- 1027What must be done with the accessible portion of abandoned fire alarm cable?
- 1028Cable ties used to secure fire alarm cables in a plenum space must have what property?
- 1029What is the minimum conductor size permitted for NPLFA circuits?
- 1030What is the maximum overcurrent protection for 18 AWG NPLFA conductors?
- 1031What is the minimum insulation voltage rating for NPLFA conductors?
- 1032Which equipment marking does NFPA 70 require where a power supply provides PLFA circuits?
- 1033A contractor wants to run PLFA cable in an elevator hoistway. What does NFPA 70 require?
- 1034What NEC rule governs fire alarm cable penetrations through fire resistance rated walls?
- 1035Which NFPA 70 article primarily covers fire alarm system wiring?
- 1036PLFA conductors and NPLFA conductors must terminate in the same control unit enclosure. What does NFPA 70 require?
- 1037Which suffix identifies a cable that has been tested to keep circuit integrity during a fire for a specified rating, such as 2 hours?
- 1038What NFPA 70 requirement applies to fire alarm circuits that are installed behind panels designed to allow access, such as lift-out ceiling tiles?
- 1039Before installing devices on a new project, what is the first document a Level II technician should compare against field conditions to build a work plan?
- 1040During rough-in, the technician finds that a duct now sits where a smoke detector is shown on the approved drawing. What is the correct action?
- 1041Which item must be installed so that the fire alarm system wiring does not degrade over time and terminations stay reliable?
- 1042What does NFPA 72 require for the primary power source of a fire alarm system?
- 1043Which mechanical protection is required for the fire alarm branch circuit disconnecting means?
- 1044Where can conductors of a Class A NAC be allowed to share a single conduit for the outgoing and return run without violating the separation rule?
- 1045Where must a smoke detector used for elevator recall be located?
- 1046Which kind of detector is normally used to initiate elevator power shutdown (shunt trip) before sprinklers discharge in the machine room?
- 1047For elevator shunt trip, how close must the heat detector be to each sprinkler head it protects?
- 1048Which signal should a sprinkler waterflow switch with retard delay produce, and what is the maximum delay allowed before the alarm is initiated?
- 1049What is the nominal spacing for spot-type smoke detectors on a smooth ceiling when no other spacing is specified?
- 1050Using the 0.7S rule with a 30 ft nominal spacing, every point on a smooth ceiling must be within what distance of a smoke detector?
- 1051With smooth ceiling spacing of 30 ft, what is the maximum distance from a wall to the nearest row of spot smoke detectors?
- 1052A spot smoke detector is to be mounted on a sidewall instead of the ceiling. Where must its top edge be?
- 1053What minimum distance should a spot smoke detector be from a forced air supply diffuser?
- 1054On a peaked ceiling, where must the first row of smoke detectors be installed?
- 1055How is spacing determined for spot-type heat detectors?
- 1056A heat detector listed for 50 ft spacing will be installed on a smooth ceiling 15 ft high. The reduction factor for a ceiling height above 14 ft up to 16 ft is 0.77. What is the adjusted spacing?
- 1057A heat detector with a listed spacing of 30 ft will be installed on a 12.5 ft high ceiling. The multiplier above 12 ft up to 14 ft is 0.84. What spacing must be used?
- 1058Where should a sidewall mounted spot heat detector be located?
- 1059On a ceiling with solid joists, how is heat detector spacing adjusted in the direction perpendicular to the joists?
- 1060What governs the spacing and mounting of projected beam smoke detectors?
- 1061Why must projected beam smoke detectors be mounted on stable surfaces?
- 1062Can a duct smoke detector be used in place of open area smoke detection?
- 1063What must be verified when installing a duct smoke detector with sampling tubes?
- 1064Where is a duct smoke detector placed on the supply side of an air handling system under NFPA 90A?
- 1065What is the mounting height range for the operable part of a manual fire alarm box?
- 1066Where must manual fire alarm boxes be located relative to exit doorways?
- 1067What is the maximum travel distance to the nearest manual fire alarm box?
- 1068A grouped opening of exit doors is 60 ft wide. Where are manual fire alarm boxes required?
- 1069What is the required mounting height for wall mounted visible notification appliances?
- 1070What range of flash rate is permitted for visible notification appliances?
- 1071When more than two visible appliances are in any field of view, what is required?
- 1072What minimum effective intensity must a visible appliance have in a sleeping area when the lens is less than 24 in. below the ceiling?
- 1073In a sleeping room, a visible appliance must be within what horizontal distance of the pillow?
- 1074A ceiling mounted strobe is to cover a square room on a 10 ft ceiling. Why can't the wall mounted candela table be used for it?
- 1075Where should a wall mounted audible notification appliance be installed?
- 1076In public mode, an audible signal must exceed the average ambient sound level by at least how much?
- 1077In private mode (for example, a staff only area), an audible signal must exceed the average ambient sound by at least how much?
- 1078At what height above the floor are audible notification levels measured for compliance?
- 1079What audible signal frequency is required to awaken occupants in sleeping areas?
- 1080In sleeping areas, which audible level is required at the pillow?
- 1081What is the maximum sound pressure level a fire alarm audible signal may produce?
- 1082What is the purpose of system commissioning before the acceptance test?
- 1083During an initial acceptance test, which devices must be tested?
- 1084Before connecting field wiring to the control unit, which test checks for unintended grounds and stray voltage on new circuits?
- 1085What instrument is used to measure insulation resistance of new fire alarm conductors to ground?
- 1086Where must spot smoke detectors be installed relative to a ceiling fan blade?
- 1087A smoke detector is planned in a room where the ambient temperature can reach 120 F. What must the technician verify?
- 1088Why should smoke detectors generally not be installed until construction cleanup is complete?
- 1089Which detector type should be chosen for an area where smoldering fires are expected to produce large, visible smoke particles?
- 1090What wiring method is used to connect a fire alarm system to a sprinkler valve tamper switch?
- 1091A valve supervisory switch must initiate a signal within what amount of valve movement?
- 1092A combination system shares a control unit for fire alarm and security functions. What must the installer make sure of?
- 1093What is the purpose of an end of line resistor on a conventional Class B initiating device circuit?
- 1094Where must the end of line resistor of a Class B circuit be installed?
- 1095When wiring to an initiating device, why must the circuit conductor be broken at each terminal rather than looped (T-tapped) on a conventional Class B circuit?
- 1096Which type of short circuit isolator placement allows a Class X SLC to keep operating after a single short?
- 1097Which records must be completed for a new system and given to the owner after acceptance?
- 1098In a corridor not more than 20 ft wide, how far apart may visible appliances be spaced under the corridor rule of NFPA 72 (2022)?
- 1099A wall mounted visible appliance must cover a 20 ft by 20 ft room by itself. What minimum effective intensity does the wall mounted room table require?
- 1100A 40 ft by 40 ft room will be covered by one wall mounted strobe. What minimum effective intensity does the wall mounted room table require?
- 1101Which control function is commonly wired from a fire alarm relay to release magnetically held smoke doors?
- 1102Where must the relay or control module that operates an emergency control function be located?
- 1103How are HVAC fan shutdown circuits typically installed when they are not monitored for integrity?
- 1104What must happen to the fire alarm system when an emergency control function interface relay fails?
- 1105Which interface must be provided so that elevators are not recalled to a floor where the lobby detector is in alarm?
- 1106What should a technician do before connecting the fire alarm system to the supervising station during installation?
- 1107Which of these devices is used to check that a wireless (low power radio) initiating device will communicate reliably before final installation?
- 1108How long may a low power radio (wireless) initiating device take to report an alarm signal to the control unit?
- 1109A technician installs a heat detector in an attic where temperatures reach 170 F. Which temperature rating classification is most appropriate?
- 1110What minimum difference is required between a fixed temperature heat detector's rating and the maximum expected ambient ceiling temperature?
- 1111In which situation is a rate of rise heat detector a poor choice?
- 1114When should notification appliances be installed relative to finishes like paint?
- 1115Which mounting rule applies when a detector is installed in an air sampling or pipe network for aspirating smoke detection?
- 1116What is the maximum transport time from the most remote sampling port of an air sampling detector to the detector?
- 1117Before starting rough-in, what should the technician confirm about the building's sprinkler system for a waterflow interface?
- 1118What is the maximum height above the floor for the highest operable switch or indicator on a fire alarm control unit display, unless the AHJ approves otherwise?
- 1119What is the minimum height above the floor for the lowest switch or bottom of the text display on a fire alarm control unit?
- 1120Which device type must be installed in an elevator hoistway that has sprinklers at the top, to support elevator recall?
Maintenance
- 2001How often must the sensitivity of system smoke detectors be checked after the first check?
- 2002When must the first sensitivity check of a newly installed smoke detector be done?
- 2003Which of these methods is NOT an acceptable way to check smoke detector sensitivity?
- 2004A smoke detector's sensitivity is found outside its listed and marked range. What must be done?
- 2005How often are restorable spot heat detectors functionally tested?
- 2006What is required for nonrestorable fixed temperature spot heat detectors after 15 years in service?
- 2007How often are manual fire alarm boxes tested?
- 2008How often are notification appliances (horns, strobes, speakers) tested?
- 2009How often are sprinkler waterflow alarm devices (vane or pressure type) tested?
- 2010How often are valve supervisory (tamper) switches tested?
- 2011How often are duct smoke detectors functionally tested?
- 2012Which test is part of the duct smoke detector inspection, beyond the smoke entry test?
- 2013What is the minimum frequency for testing fire alarm control unit functions (alarm, supervisory, trouble signals) in a monitored system?
- 2014Who must perform inspection, testing, and maintenance of a fire alarm system?
- 2015Before testing begins in an occupied building, whom must the technician notify?
- 2016After testing is complete, what must the technician do with persons notified before the test?
- 2017Who is responsible for the inspection, testing, and maintenance of a fire alarm system?
- 2019Which visual inspection frequency applies to waterflow and supervisory devices under NFPA 72 (2022)?
- 2020How often should the fire alarm control unit receive a visual inspection when the system is monitored for alarm, supervisory, and trouble signals?
- 2021How often must a control unit that is NOT monitored for alarm, supervisory, and trouble signals be visually inspected?
- 2022What is the purpose of a visual inspection before a functional test of devices?
- 2023A new wall was built in an open office, splitting a room so one part has no smoke detector. Which inspection step should catch this?
- 2025What test equipment is typically used for annual functional testing of spot smoke detectors in place?
- 2026What is the correct way to functionally test a restorable heat detector?
- 2027A technician bypasses a zone for testing and forgets to restore it. What risk does this create?
- 2028The control unit shows a ground fault trouble. What is the most efficient first step to locate it?
- 2029A technician measures resistance from one conductor of a disconnected circuit to a known building ground. Which reading suggests a ground fault?
- 2030With field wiring disconnected and the far end of a Class B IDC open (EOL removed), what reading between the two conductors indicates a short?
- 2031A Class B IDC with a 4.7 kilohm EOL resistor reads infinite resistance at the panel terminals with field wiring removed. What does this indicate?
- 2032A 24 VDC NAC with a 2.2 kilohm EOL is checked with the panel in normal (supervisory) condition. Which measurement confirms the EOL is in place?
- 2033Why are notification appliances on a supervised NAC polarized (diode blocked)?
- 2034Using Ohm's law, a circuit draws 0.5 A at 24 V. What is the circuit resistance?
- 2035A 24 VDC fire alarm relay coil has a resistance of 1200 ohms. What current does it draw?
- 2036A 24 VDC panel power supply delivers 3 A to its load. How much power is that?
- 2037Two 4.7 kilohm resistors are accidentally connected in parallel at the end of an IDC. What resistance does the panel see?
- 2038A technician measures 18.2 V at the last strobe on a NAC while the panel output reads 24.0 V in alarm. What is the voltage drop on the circuit?
- 2039Strobes on the end of a NAC flash dimly and some do not flash at all during the alarm test, while the first strobes work. What is the most likely cause?
- 2040A technician finds that an addressable smoke detector reports a different device type than programmed. What type of trouble will the panel show?
- 2041Two addressable devices are set to the same address on an SLC. What is the typical result?
- 2042What does a trouble signal indicate in a fire alarm system?
- 2043Which of these conditions should produce a supervisory signal rather than a trouble signal?
- 2044A trouble signal must be annunciated within what time after the fault occurs?
- 2045When a trouble signal is silenced at the panel and the fault is not repaired, what happens?
- 2046What must the technician do when a system impairment is found during a service visit?
- 2047Which actions are part of a planned impairment procedure under NFPA 72?
- 2048After repairing a deficiency, what testing must be done?
- 2049After a change to site specific software, how many initiating devices not directly affected by the change must be tested?
- 2050A software change affects 3 devices. The system has 380 initiating devices total. How many unaffected devices must also be tested?
- 2051A site specific software change is made on a system with 1200 initiating devices. What is the maximum number of unaffected devices required to be tested?
- 2052When the control unit firmware (executive software) is changed, what must be done?
- 2053How long must records of inspection, testing, and maintenance be retained?
- 2054How long must the original acceptance test records be retained?
- 2055Where must a copy of the site specific software be kept?
- 2057How must the documentation cabinet be labeled?
- 2058What information must be recorded for each device tested in an ITM report?
- 2059Which battery marking must be on every secondary supply battery?
- 2060Under NFPA 72 (2022), what applies to rechargeable batteries used as the secondary power supply starting January 1, 2024?
- 2061Which visual condition of a sealed lead acid battery calls for immediate replacement?
- 2062What is a typical float charge voltage for a 24 V sealed lead acid battery set (two 12 V batteries)?
- 2063During an annual test, the panel is switched from primary to secondary power. What should be verified?
- 2064What is the typical end voltage used for a 24 V battery set at the end of its required standby and alarm period?
- 2065How often must the month and year marking on sealed (VRLA) batteries be checked against the manufacturer replacement date?
- 2066How is a fire alarm audible appliance's sound level checked when the ambient noise in an area has changed since acceptance?
- 2068A technician arrives for an annual test and finds a smoke detector covered with a plastic bag. What should be done?
- 2069Why should alarm verification be checked during periodic testing of smoke detector circuits?
- 2070What is the maximum alarm verification time allowed for smoke detectors under NFPA 72?
- 2071Which testing practice prevents unnecessary fire department response during an annual test?
- 2072What must be tested on the supervising station transmitter during periodic testing?
- 2073A dual path communicator loses its cellular path but keeps its IP path. What must the system do?
- 2074When replacing a failed addressable smoke detector with a new one, what must the technician verify?
- 2075Which document should be used to confirm the correct operation of each input and output during testing?
- 2076A technician finds several corroded terminals in an outdoor junction box on an IDC. Which fault is most likely to result?
- 2077An SLC with 60 addressable devices has a ground fault. The technician lifts the field wiring at device 30 and the ground fault trouble clears. Where is the fault?
- 2078A ground fault trouble appears only during heavy rain and clears in dry weather. What is the most likely cause?
- 2079A Class A IDC shows an open circuit trouble, yet every device on it still alarms when tested. Why?
- 2080A short circuit occurs on a Class A SLC that has isolator modules between groups of devices. What is the expected result?
- 2081A NAC has 12 strobes. The technician removes the EOL resistor and measures resistance across the disconnected field conductors with the meter leads in normal polarity. The reading is a few ohms. What does it indicate?
- 2082During an annual test, a horn strobe works on AC power but fails to operate after the panel transfers to batteries. Which is the most likely cause?
- 2083A technician measures 20.8 V at the last appliance in alarm with the panel on batteries. The appliances are listed for 16 V to 33 V. What is the conclusion?
- 2084A strobe NAC draws 2.4 A in alarm. The run is 250 ft one way of 12 AWG solid copper (1.93 ohms per 1000 ft). What is the voltage drop, treating the load at the end?
- 2085An owner asks to add 6 strobes drawing 0.15 A each to an existing NAC that already draws 1.7 A. The NAC is rated 2.5 A. What is the new load?
- 2086A system's measured standby current is 0.45 A and alarm current is 2.8 A. It requires 24 h standby plus 5 min alarm, with the 1.25 aging correction factor applied. What minimum battery capacity is needed?
- 2087An annual test of a 24 V sealed lead acid battery set is done. Which test shows whether the batteries can deliver their rated capacity?
- 2088How often must the battery charger of a fire alarm control unit be tested?
- 2089How are projected beam smoke detectors tested in the field?
- 2090During the annual test of an air sampling smoke detection system, what must be checked from the most remote sampling port?
- 2091How should a multicriteria detector (for example smoke plus heat) be functionally tested?
- 2092A carbon monoxide detector connected to the fire alarm system signals end of life. What must be done?
- 2093How often must door release, fan shutdown, and other emergency control functions be tested?
- 2094During an annual test, a duct smoke detector alarms but the air handler keeps running. Which item should be checked first?
- 2095An emergency voice/alarm communication system is tested. What must be verified for the speakers in each acoustically distinguishable space?
- 2096A technician is asked to replace a failed 24 V power supply board with one from a different manufacturer. What applies?
- 2097Smoke from a test aerosol triggers a detector, but the panel shows the alarm about 60 s later than expected. What feature is most likely enabled?
- 2098A remote annunciator shows a different zone description than the main panel for the same device. What should the technician do?
- 2099When should a fire alarm system service technician tag a device or system as impaired?
- 2100A smoke detector in a dusty warehouse keeps showing a maintenance alert. What is the correct response?
- 2101Ambient noise in a manufacturing room has risen to an average of 82 dBA since acceptance. The system operates in public mode. What minimum alarm level is needed now?
- 2102Two identical horns each produce 78 dBA at a test point when sounded alone. What level should be expected at that point with both sounding?
- 2103A horn measures 88 dBA at 10 ft. Assuming free field loss, what level is expected at 40 ft?
- 2104After an inspection, the service company finds deficiencies it cannot fix that day. What must the report include?
- 2105A technician measures 4.2 kilohms across a Class B IDC at the panel with field wiring disconnected. The EOL is 4.7 kilohms. What is the most likely issue?
Submittal Preparation and System Layout
- 3001Which item must be shown on fire alarm shop drawings submitted for approval?
- 3002Which document gives the reviewer the logic of what each input does to each output?
- 3003What does a riser diagram show on a fire alarm shop drawing set?
- 3004Which calculation must be included with the shop drawings for a system with secondary power from batteries?
- 3005Which sheet item helps the reviewer confirm each wall mounted strobe will cover its room?
- 3006What must record drawings show at the end of a project?
- 3007Before laying out devices in an existing building, what is the purpose of a site survey?
- 3008Which ceiling condition found during a site survey changes smoke detector spacing?
- 3009A smooth ceiling room is 60 ft by 90 ft. Detectors are laid out on a 30 ft grid. How many spot smoke detectors are needed?
- 3010A corridor is 10 ft wide. Using the 0.7S rule with S = 30 ft (every point within 21 ft of a detector), what is the maximum spacing between detectors along the centerline?
- 3011A heat detector listed for 50 ft spacing is planned for a 20 ft ceiling. The multiplier for 20 ft is 0.64. What spacing applies?
- 3012A room is 40 ft by 64 ft with a 20 ft smooth ceiling. Heat detectors are listed for 50 ft (adjusted spacing 32 ft). What is the minimum detector count on a square grid?
- 3013A projected beam detector is listed for a maximum beam length of 330 ft and a width of 60 ft. How far from the side wall may the beam be placed?
- 3014A 20 ft by 30 ft room has a 10 ft ceiling and will use one wall mounted strobe in the middle of the long wall. Which room size must be used to pick the candela?
- 3015A room is 30 ft by 30 ft with one wall mounted strobe. What minimum effective intensity applies?
- 3016A 24 V battery set must support a standby load of 0.32 A for 24 h and an alarm load of 3.6 A for 5 min. Apply the 1.25 aging correction factor of NFPA 72 (2022/2025). What capacity is required?
- 3017An emergency voice/alarm communication system has a standby load of 1.1 A and an alarm load of 6.0 A. It needs 24 h standby and 15 min of alarm, with the 1.25 aging correction factor applied. What capacity is required?
- 3018What is the required standby duration for the secondary power supply of a typical building fire alarm system before the alarm period?
- 3019A NAC uses 14 AWG stranded copper (3.14 ohms per 1000 ft). The appliances draw 1.5 A in total and the farthest one is 300 ft from the panel. What is the voltage drop, treating the load at the end?
- 3020A designer starts at 20.4 V (battery end voltage) and needs at least 16.0 V at the last appliance. The NAC draws 2.0 A and uses 12 AWG solid (1.93 ohms per 1000 ft). What is the maximum one way length, with the load at the end?
- 3021Under the IBC, when is a manual fire alarm system required in a Group A occupancy?
- 3022Under the IBC, what happens when the fire alarm activates in a Group A occupancy with an occupant load of 1,000 or more?
- 3023Under the IBC, when is a manual fire alarm system required in a Group B occupancy?
- 3024Under the IBC, a Group E occupancy needs a manual fire alarm system at what occupant load?
- 3025Under the IBC, when is a manual fire alarm system required in a Group M occupancy?
- 3026Under the IBC, which condition requires a manual fire alarm system in a Group R-2 apartment building?
- 3027Under the IBC, what fire alarm features are required in a Group R-1 hotel?
- 3028Under the IBC, when is a manual fire alarm system required in a Group F occupancy?
- 3029Under the IBC, which fire alarm requirement applies to Group I occupancies?
- 3030Under the IBC, a building is fully sprinklered and the occupant notification activates on sprinkler waterflow. What does the common exception allow for Group B or M?
- 3031Under the IBC, what is the maximum area of one fire alarm zone?
- 3032A single floor of a building covers 60,000 sq ft. What is the minimum number of IBC fire alarm zones for that floor?
- 3033A three story office building has floors of 12,000 sq ft each. How many IBC fire alarm zones are needed at minimum?
- 3034Under the IBC, what spare capacity must notification appliance circuits in employee work areas have when audible coverage is provided there?
- 3035Under the IBC, where must visible alarm notification appliances be provided?
- 3036Under the IMC, an air distribution system has a design capacity over what airflow before a smoke detector is required in the return air?
- 3037Under the IBC, a duct smoke detector connected to a building fire alarm system activates. What signal is required?
- 3038Under the IBC, how must smoke alarms in a dwelling unit with more than one alarm be connected?
- 3039Under the IBC, which feature is required in high rise buildings for occupant notification?
- 3040Which section of NFPA 101 contains the general requirements for fire detection, alarm, and communication systems?
- 3041A 500 ft long corridor has an exit at each end. Manual boxes are placed within 5 ft of each exit. How many manual boxes are needed at minimum on that floor to meet the 200 ft travel distance?
- 3042A floor has four exit stairs and the travel distance to the nearest of them is always under 150 ft. How many manual boxes are needed on that floor?
- 3043A room is 45 ft by 75 ft with a smooth 10 ft ceiling. Using 30 ft spacing for spot smoke detectors, what is the minimum count on a regular grid?
- 3044A heat detector listed for 30 ft spacing is installed on a 15 ft smooth ceiling. The multiplier for that height is 0.77. What is the adjusted spacing?
- 3045On a 12 ft ceiling, beams are 8 in. deep. How are the beams treated for spot smoke detector spacing?
- 3046Under NFPA 90A, an air handler has a supply capacity of 18,000 cfm. Where is a duct smoke detector needed on the supply side?
- 3047A design uses 18 strobes at 0.12 A and 10 horns at 0.03 A on one NAC. What is the alarm current?
- 3048Why should NAC current calculations use the appliance current at the low end of its operating voltage range?
- 3049A booster power supply is rated 8.0 A total. Its NACs serve 7.2 A of alarm load. What percentage of its capacity is used?
- 3050A small system has a standby load of 0.18 A and an alarm load of 1.9 A. It needs 24 h standby and 5 min alarm, with the 1.25 aging correction factor applied. Which standard battery size is the smallest that works?
- 3051Since the 2022 edition, what minimum correction factor must NFPA 72 battery calculations apply to the calculated amp-hour capacity to allow for battery aging?
- 3052A NAC run is 200 ft one way using 16 AWG stranded copper (4.99 ohms per 1000 ft). The alarm load is 1.0 A at the end. What is the voltage drop?
- 3053A NAC must deliver 2.5 A at 400 ft one way, and the allowed drop is 3.4 V. Which is the smallest solid copper conductor that works? (12 AWG = 1.93, 10 AWG = 1.21 ohms per 1000 ft)
- 3054Why does treating the whole NAC load as if it were at the last appliance give a conservative voltage drop result?
- 3055A 25 V speaker circuit serves 32 speakers tapped at 1 W and 8 speakers tapped at 2 W. What total power does the amplifier need to supply?
- 3056Average ambient sound in an office is 60 dBA. A horn produces 90 dBA at 10 ft. In public mode, would a person 80 ft away (free field) meet the required level?
- 3057Why should ambient sound levels be measured during the site survey of an existing building?
- 3058Corridor horns must awaken occupants in hotel rooms behind closed doors. What layout concern applies?
- 3059Which of these items is a required part of the floor plan on fire alarm shop drawings?
- 3060Why must shop drawings show ceiling heights and ceiling construction for each area?
- 3061Which documents are typically part of a fire alarm submittal package besides the drawings?
- 3062Who completes the record of completion for a new fire alarm system?
- 3063When a system is modified after acceptance, what must happen to the record documentation?
- 3064Which item on a shop drawing helps reviewers confirm the correct cable type for each area?
- 3065A design shows a notification zone layout for partial evacuation. Which information must the drawings make clear?
- 3066What is the main purpose of a fire alarm system's sequence of operation for the AHJ?
- 3067A design places a spot smoke detector 2 ft from a supply diffuser. What should the reviewer note?
- 3068A design calls for a sidewall mounted smoke detector. What placement must the drawing show?
- 3069Which standby duration does NFPA 72 require for the secondary power of an emergency voice/alarm communication system in alarm?
- 3070Which equipment locations must the shop drawings show besides initiating devices and appliances?
- 3071When should fire alarm shop drawings normally be approved by the AHJ?
- 3072A heat detector listed for 25 ft spacing is installed on an 11 ft smooth ceiling. The multiplier for that height is 0.91. What is the adjusted spacing?
- 3073A heat detector listed for 50 ft spacing is planned for a 30 ft ceiling. The multiplier is 0.34. What spacing applies?
- 3074A 20 ft wide room uses spot smoke detectors with S = 30 ft. Every point must be within 21 ft of a detector. With one row down the center, what is the maximum spacing along the row?
- 3075A speaker set on its 1 W tap produces 84 dBA at 10 ft. What level is expected at 10 ft on the 2 W tap?
- 3076An SLC is limited by the manufacturer to 40 ohms of total loop resistance. Using 18 AWG solid (7.77 ohms per 1000 ft), what is the maximum one way distance for a Class B run to the farthest device?
- 3077Within what time must the battery charger be able to recharge fully discharged secondary batteries?
- 3078Where must a smoke detector in an elevator lobby be placed in relation to the elevator doors?
- 3079A design adds new detectors to an existing panel from a different manufacturer. What must the designer confirm?
- 3080Which documents must be provided to the owner at the completion of a new system?
- 3081A system uses a digital alarm communicator transmitter (DACT). What does NFPA 72 require for its transmission means?
- 3082Under the IBC, where is a two way communication system generally required for accessible means of egress in a multistory building?
- 3083What must be stated on a shop drawing title block?
- 3084Which item should a designer include so the AHJ can see how the system responds to a waterflow signal on floor 3?
- 3085A building has a 30 ft wide by 120 ft long room with a smooth 12 ft ceiling. Spot smoke detectors use S = 30 ft. How many are needed in a single row down the center?
- 3086On a shop drawing, what does the symbol legend do?
- 3087Why must shop drawings show the location of the building's sprinkler riser and control valves?
- 3088A designer must produce battery calculations. Which current values should be used for each device?
- 3089A design places two smoke detectors 28 ft apart in a room with a smooth 10 ft ceiling. Each is 10 ft from the side walls. Does this meet the 30 ft spacing rule?
- 3090Why should notification appliance circuits be designed with some spare capacity?
Management and Supervision
- 4001When a portable ladder is used to reach an upper landing, how far must its side rails extend above the landing?
- 4002A non self supporting ladder is 16 ft long from base to support point. How far should the base be from the wall?
- 4003In construction, at what height above a lower level must workers on unprotected sides and edges have fall protection?
- 4004At what height do workers on a scaffold need fall protection under OSHA construction rules?
- 4005A technician must service a 120 V circuit feeding a fire alarm booster power supply. Under OSHA lockout/tagout rules, who may remove the lock afterward?
- 4006Which receptacles on a construction site need ground fault protection under OSHA when an assured equipment grounding program is not used?
- 4007A technician must enter a below grade vault with limited entry and possible hazardous atmosphere to reach a junction box. What applies?
- 4008Where must safety data sheets for chemicals used on a job, such as aerosol smoke or cleaning solvents, be available?
- 4009Which practice is prohibited when using a stepladder?
- 4010A technician uses a boom lift to install beam detectors. What fall protection is required?
- 4011What minimum clearance should be kept from overhead power lines of 50 kV or less when working with ladders or equipment?
- 4012A crew must work near exposed energized parts in an electrical room. Which ladder type should be used?
- 4013Under AIA A201 (2017), what does the architect's review of shop drawings check?
- 4014Under AIA A201 (2017), what must the contractor do before submitting shop drawings to the architect?
- 4015Under AIA A201 (2017), which document changes the contract sum or time and is signed by the owner, contractor, and architect?
- 4016Under AIA A201 (2017), what allows the owner to direct a change before the price is agreed?
- 4017Under AIA A201 (2017), who may order a minor change in the work that does not change the contract sum or time?
- 4018Under AIA A201 (2017), within how many days after the event must a claim normally be started?
- 4019Under AIA A201 (2017), how long is the correction period after substantial completion?
- 4020Under AIA A201 (2017), who is solely responsible for construction means, methods, techniques, sequences, and procedures?
- 4021Under AIA A201 (2017), what may the architect do with a submittal that the contract documents do not require?
- 4022A Level II technician finds a conflict between the fire alarm drawings and the ceiling plan. What is the correct way to resolve it?
- 4023Before acceptance testing of elevator recall and shunt trip, which coordination is needed?
- 4024On a new building, which trade usually installs the sprinkler waterflow and tamper switches that the fire alarm contractor then wires?
- 4025Smoke detectors are installed while drywall sanding is still going on. What should the supervisor arrange?
- 4026Under the International Fire Code, a required fire alarm system is out of service. What must happen?
- 4027On a project schedule, what is the critical path?
- 4028A wire takeoff from the drawings measures 2,400 ft of cable. The supervisor adds 10 percent for waste and routing. How much cable should be ordered?
- 4029A project has 120 devices. Each takes about 0.75 labor hours to install and terminate. With a crew of two technicians, how many working hours will it take?
- 4030Why should fire alarm devices and equipment be ordered only after the submittals are approved?
- 4031Which qualification does NFPA 72 accept for personnel who perform inspection, testing, and maintenance?
- 4032At the start of each work day on a fire alarm job, which supervisor action best supports safe and efficient work?
- 4033A customer asks the technician to disable a nuisance detector permanently. What should the supervisor do?
- 4034Which record helps a supervisor prove what work was done on a given day on site?
- 4035A crew must braze a pipe support near an area with active smoke detectors. Which step should the supervisor arrange first?