What is required for nonrestorable fixed temperature spot heat detectors after 15 years in service?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2006
- B: Replace them, or lab test 2 per 100
Explanation
Nonrestorable spot heat detectors cannot be heat tested in place. After 15 years they are replaced, or 2 per 100 are removed and laboratory tested, with more tested or all replaced if a failure occurs.