NICET Fire Alarm Systems Level II, Maintenance: all 101 questions
All questions from the Maintenance section for NICET Fire Alarm Systems Level II, each with the correct answer.
- 2001How often must the sensitivity of system smoke detectors be checked after the first check?
- 2002When must the first sensitivity check of a newly installed smoke detector be done?
- 2003Which of these methods is NOT an acceptable way to check smoke detector sensitivity?
- 2004A smoke detector's sensitivity is found outside its listed and marked range. What must be done?
- 2005How often are restorable spot heat detectors functionally tested?
- 2006What is required for nonrestorable fixed temperature spot heat detectors after 15 years in service?
- 2007How often are manual fire alarm boxes tested?
- 2008How often are notification appliances (horns, strobes, speakers) tested?
- 2009How often are sprinkler waterflow alarm devices (vane or pressure type) tested?
- 2010How often are valve supervisory (tamper) switches tested?
- 2011How often are duct smoke detectors functionally tested?
- 2012Which test is part of the duct smoke detector inspection, beyond the smoke entry test?
- 2013What is the minimum frequency for testing fire alarm control unit functions (alarm, supervisory, trouble signals) in a monitored system?
- 2014Who must perform inspection, testing, and maintenance of a fire alarm system?
- 2015Before testing begins in an occupied building, whom must the technician notify?
- 2016After testing is complete, what must the technician do with persons notified before the test?
- 2017Who is responsible for the inspection, testing, and maintenance of a fire alarm system?
- 2019Which visual inspection frequency applies to waterflow and supervisory devices under NFPA 72 (2022)?
- 2020How often should the fire alarm control unit receive a visual inspection when the system is monitored for alarm, supervisory, and trouble signals?
- 2021How often must a control unit that is NOT monitored for alarm, supervisory, and trouble signals be visually inspected?
- 2022What is the purpose of a visual inspection before a functional test of devices?
- 2023A new wall was built in an open office, splitting a room so one part has no smoke detector. Which inspection step should catch this?
- 2025What test equipment is typically used for annual functional testing of spot smoke detectors in place?
- 2026What is the correct way to functionally test a restorable heat detector?
- 2027A technician bypasses a zone for testing and forgets to restore it. What risk does this create?
- 2028The control unit shows a ground fault trouble. What is the most efficient first step to locate it?
- 2029A technician measures resistance from one conductor of a disconnected circuit to a known building ground. Which reading suggests a ground fault?
- 2030With field wiring disconnected and the far end of a Class B IDC open (EOL removed), what reading between the two conductors indicates a short?
- 2031A Class B IDC with a 4.7 kilohm EOL resistor reads infinite resistance at the panel terminals with field wiring removed. What does this indicate?
- 2032A 24 VDC NAC with a 2.2 kilohm EOL is checked with the panel in normal (supervisory) condition. Which measurement confirms the EOL is in place?
- 2033Why are notification appliances on a supervised NAC polarized (diode blocked)?
- 2034Using Ohm's law, a circuit draws 0.5 A at 24 V. What is the circuit resistance?
- 2035A 24 VDC fire alarm relay coil has a resistance of 1200 ohms. What current does it draw?
- 2036A 24 VDC panel power supply delivers 3 A to its load. How much power is that?
- 2037Two 4.7 kilohm resistors are accidentally connected in parallel at the end of an IDC. What resistance does the panel see?
- 2038A technician measures 18.2 V at the last strobe on a NAC while the panel output reads 24.0 V in alarm. What is the voltage drop on the circuit?
- 2039Strobes on the end of a NAC flash dimly and some do not flash at all during the alarm test, while the first strobes work. What is the most likely cause?
- 2040A technician finds that an addressable smoke detector reports a different device type than programmed. What type of trouble will the panel show?
- 2041Two addressable devices are set to the same address on an SLC. What is the typical result?
- 2042What does a trouble signal indicate in a fire alarm system?
- 2043Which of these conditions should produce a supervisory signal rather than a trouble signal?
- 2044A trouble signal must be annunciated within what time after the fault occurs?
- 2045When a trouble signal is silenced at the panel and the fault is not repaired, what happens?
- 2046What must the technician do when a system impairment is found during a service visit?
- 2047Which actions are part of a planned impairment procedure under NFPA 72?
- 2048After repairing a deficiency, what testing must be done?
- 2049After a change to site specific software, how many initiating devices not directly affected by the change must be tested?
- 2050A software change affects 3 devices. The system has 380 initiating devices total. How many unaffected devices must also be tested?
- 2051A site specific software change is made on a system with 1200 initiating devices. What is the maximum number of unaffected devices required to be tested?
- 2052When the control unit firmware (executive software) is changed, what must be done?
- 2053How long must records of inspection, testing, and maintenance be retained?
- 2054How long must the original acceptance test records be retained?
- 2055Where must a copy of the site specific software be kept?
- 2057How must the documentation cabinet be labeled?
- 2058What information must be recorded for each device tested in an ITM report?
- 2059Which battery marking must be on every secondary supply battery?
- 2060Under NFPA 72 (2022), what applies to rechargeable batteries used as the secondary power supply starting January 1, 2024?
- 2061Which visual condition of a sealed lead acid battery calls for immediate replacement?
- 2062What is a typical float charge voltage for a 24 V sealed lead acid battery set (two 12 V batteries)?
- 2063During an annual test, the panel is switched from primary to secondary power. What should be verified?
- 2064What is the typical end voltage used for a 24 V battery set at the end of its required standby and alarm period?
- 2065How often must the month and year marking on sealed (VRLA) batteries be checked against the manufacturer replacement date?
- 2066How is a fire alarm audible appliance's sound level checked when the ambient noise in an area has changed since acceptance?
- 2068A technician arrives for an annual test and finds a smoke detector covered with a plastic bag. What should be done?
- 2069Why should alarm verification be checked during periodic testing of smoke detector circuits?
- 2070What is the maximum alarm verification time allowed for smoke detectors under NFPA 72?
- 2071Which testing practice prevents unnecessary fire department response during an annual test?
- 2072What must be tested on the supervising station transmitter during periodic testing?
- 2073A dual path communicator loses its cellular path but keeps its IP path. What must the system do?
- 2074When replacing a failed addressable smoke detector with a new one, what must the technician verify?
- 2075Which document should be used to confirm the correct operation of each input and output during testing?
- 2076A technician finds several corroded terminals in an outdoor junction box on an IDC. Which fault is most likely to result?
- 2077An SLC with 60 addressable devices has a ground fault. The technician lifts the field wiring at device 30 and the ground fault trouble clears. Where is the fault?
- 2078A ground fault trouble appears only during heavy rain and clears in dry weather. What is the most likely cause?
- 2079A Class A IDC shows an open circuit trouble, yet every device on it still alarms when tested. Why?
- 2080A short circuit occurs on a Class A SLC that has isolator modules between groups of devices. What is the expected result?
- 2081A NAC has 12 strobes. The technician removes the EOL resistor and measures resistance across the disconnected field conductors with the meter leads in normal polarity. The reading is a few ohms. What does it indicate?
- 2082During an annual test, a horn strobe works on AC power but fails to operate after the panel transfers to batteries. Which is the most likely cause?
- 2083A technician measures 20.8 V at the last appliance in alarm with the panel on batteries. The appliances are listed for 16 V to 33 V. What is the conclusion?
- 2084A strobe NAC draws 2.4 A in alarm. The run is 250 ft one way of 12 AWG solid copper (1.93 ohms per 1000 ft). What is the voltage drop, treating the load at the end?
- 2085An owner asks to add 6 strobes drawing 0.15 A each to an existing NAC that already draws 1.7 A. The NAC is rated 2.5 A. What is the new load?
- 2086A system's measured standby current is 0.45 A and alarm current is 2.8 A. It requires 24 h standby plus 5 min alarm, with the 1.25 aging correction factor applied. What minimum battery capacity is needed?
- 2087An annual test of a 24 V sealed lead acid battery set is done. Which test shows whether the batteries can deliver their rated capacity?
- 2088How often must the battery charger of a fire alarm control unit be tested?
- 2089How are projected beam smoke detectors tested in the field?
- 2090During the annual test of an air sampling smoke detection system, what must be checked from the most remote sampling port?
- 2091How should a multicriteria detector (for example smoke plus heat) be functionally tested?
- 2092A carbon monoxide detector connected to the fire alarm system signals end of life. What must be done?
- 2093How often must door release, fan shutdown, and other emergency control functions be tested?
- 2094During an annual test, a duct smoke detector alarms but the air handler keeps running. Which item should be checked first?
- 2095An emergency voice/alarm communication system is tested. What must be verified for the speakers in each acoustically distinguishable space?
- 2096A technician is asked to replace a failed 24 V power supply board with one from a different manufacturer. What applies?
- 2097Smoke from a test aerosol triggers a detector, but the panel shows the alarm about 60 s later than expected. What feature is most likely enabled?
- 2098A remote annunciator shows a different zone description than the main panel for the same device. What should the technician do?
- 2099When should a fire alarm system service technician tag a device or system as impaired?
- 2100A smoke detector in a dusty warehouse keeps showing a maintenance alert. What is the correct response?
- 2101Ambient noise in a manufacturing room has risen to an average of 82 dBA since acceptance. The system operates in public mode. What minimum alarm level is needed now?
- 2102Two identical horns each produce 78 dBA at a test point when sounded alone. What level should be expected at that point with both sounding?
- 2103A horn measures 88 dBA at 10 ft. Assuming free field loss, what level is expected at 40 ft?
- 2104After an inspection, the service company finds deficiencies it cannot fix that day. What must the report include?
- 2105A technician measures 4.2 kilohms across a Class B IDC at the panel with field wiring disconnected. The EOL is 4.7 kilohms. What is the most likely issue?