Average ambient sound in an office is 60 dBA. A horn produces 90 dBA at 10 ft. In public mode, would a person 80 ft away (free field) meet the required level?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3056
- B: No, about 72 dBA is expected and 75 dBA is needed
Explanation
Required = 60 + 15 = 75 dBA. From 10 ft to 80 ft is three doublings, so the level is 90 - 18 = 72 dBA. Another horn closer to that area is needed.