NICET Fire Alarm Systems Level II, Submittal Preparation and System Layout: all 90 questions
All questions from the Submittal Preparation and System Layout section for NICET Fire Alarm Systems Level II, each with the correct answer.
- 3001Which item must be shown on fire alarm shop drawings submitted for approval?
- 3002Which document gives the reviewer the logic of what each input does to each output?
- 3003What does a riser diagram show on a fire alarm shop drawing set?
- 3004Which calculation must be included with the shop drawings for a system with secondary power from batteries?
- 3005Which sheet item helps the reviewer confirm each wall mounted strobe will cover its room?
- 3006What must record drawings show at the end of a project?
- 3007Before laying out devices in an existing building, what is the purpose of a site survey?
- 3008Which ceiling condition found during a site survey changes smoke detector spacing?
- 3009A smooth ceiling room is 60 ft by 90 ft. Detectors are laid out on a 30 ft grid. How many spot smoke detectors are needed?
- 3010A corridor is 10 ft wide. Using the 0.7S rule with S = 30 ft (every point within 21 ft of a detector), what is the maximum spacing between detectors along the centerline?
- 3011A heat detector listed for 50 ft spacing is planned for a 20 ft ceiling. The multiplier for 20 ft is 0.64. What spacing applies?
- 3012A room is 40 ft by 64 ft with a 20 ft smooth ceiling. Heat detectors are listed for 50 ft (adjusted spacing 32 ft). What is the minimum detector count on a square grid?
- 3013A projected beam detector is listed for a maximum beam length of 330 ft and a width of 60 ft. How far from the side wall may the beam be placed?
- 3014A 20 ft by 30 ft room has a 10 ft ceiling and will use one wall mounted strobe in the middle of the long wall. Which room size must be used to pick the candela?
- 3015A room is 30 ft by 30 ft with one wall mounted strobe. What minimum effective intensity applies?
- 3016A 24 V battery set must support a standby load of 0.32 A for 24 h and an alarm load of 3.6 A for 5 min. Apply the 1.25 aging correction factor of NFPA 72 (2022/2025). What capacity is required?
- 3017An emergency voice/alarm communication system has a standby load of 1.1 A and an alarm load of 6.0 A. It needs 24 h standby and 15 min of alarm, with the 1.25 aging correction factor applied. What capacity is required?
- 3018What is the required standby duration for the secondary power supply of a typical building fire alarm system before the alarm period?
- 3019A NAC uses 14 AWG stranded copper (3.14 ohms per 1000 ft). The appliances draw 1.5 A in total and the farthest one is 300 ft from the panel. What is the voltage drop, treating the load at the end?
- 3020A designer starts at 20.4 V (battery end voltage) and needs at least 16.0 V at the last appliance. The NAC draws 2.0 A and uses 12 AWG solid (1.93 ohms per 1000 ft). What is the maximum one way length, with the load at the end?
- 3021Under the IBC, when is a manual fire alarm system required in a Group A occupancy?
- 3022Under the IBC, what happens when the fire alarm activates in a Group A occupancy with an occupant load of 1,000 or more?
- 3023Under the IBC, when is a manual fire alarm system required in a Group B occupancy?
- 3024Under the IBC, a Group E occupancy needs a manual fire alarm system at what occupant load?
- 3025Under the IBC, when is a manual fire alarm system required in a Group M occupancy?
- 3026Under the IBC, which condition requires a manual fire alarm system in a Group R-2 apartment building?
- 3027Under the IBC, what fire alarm features are required in a Group R-1 hotel?
- 3028Under the IBC, when is a manual fire alarm system required in a Group F occupancy?
- 3029Under the IBC, which fire alarm requirement applies to Group I occupancies?
- 3030Under the IBC, a building is fully sprinklered and the occupant notification activates on sprinkler waterflow. What does the common exception allow for Group B or M?
- 3031Under the IBC, what is the maximum area of one fire alarm zone?
- 3032A single floor of a building covers 60,000 sq ft. What is the minimum number of IBC fire alarm zones for that floor?
- 3033A three story office building has floors of 12,000 sq ft each. How many IBC fire alarm zones are needed at minimum?
- 3034Under the IBC, what spare capacity must notification appliance circuits in employee work areas have when audible coverage is provided there?
- 3035Under the IBC, where must visible alarm notification appliances be provided?
- 3036Under the IMC, an air distribution system has a design capacity over what airflow before a smoke detector is required in the return air?
- 3037Under the IBC, a duct smoke detector connected to a building fire alarm system activates. What signal is required?
- 3038Under the IBC, how must smoke alarms in a dwelling unit with more than one alarm be connected?
- 3039Under the IBC, which feature is required in high rise buildings for occupant notification?
- 3040Which section of NFPA 101 contains the general requirements for fire detection, alarm, and communication systems?
- 3041A 500 ft long corridor has an exit at each end. Manual boxes are placed within 5 ft of each exit. How many manual boxes are needed at minimum on that floor to meet the 200 ft travel distance?
- 3042A floor has four exit stairs and the travel distance to the nearest of them is always under 150 ft. How many manual boxes are needed on that floor?
- 3043A room is 45 ft by 75 ft with a smooth 10 ft ceiling. Using 30 ft spacing for spot smoke detectors, what is the minimum count on a regular grid?
- 3044A heat detector listed for 30 ft spacing is installed on a 15 ft smooth ceiling. The multiplier for that height is 0.77. What is the adjusted spacing?
- 3045On a 12 ft ceiling, beams are 8 in. deep. How are the beams treated for spot smoke detector spacing?
- 3046Under NFPA 90A, an air handler has a supply capacity of 18,000 cfm. Where is a duct smoke detector needed on the supply side?
- 3047A design uses 18 strobes at 0.12 A and 10 horns at 0.03 A on one NAC. What is the alarm current?
- 3048Why should NAC current calculations use the appliance current at the low end of its operating voltage range?
- 3049A booster power supply is rated 8.0 A total. Its NACs serve 7.2 A of alarm load. What percentage of its capacity is used?
- 3050A small system has a standby load of 0.18 A and an alarm load of 1.9 A. It needs 24 h standby and 5 min alarm, with the 1.25 aging correction factor applied. Which standard battery size is the smallest that works?
- 3051Since the 2022 edition, what minimum correction factor must NFPA 72 battery calculations apply to the calculated amp-hour capacity to allow for battery aging?
- 3052A NAC run is 200 ft one way using 16 AWG stranded copper (4.99 ohms per 1000 ft). The alarm load is 1.0 A at the end. What is the voltage drop?
- 3053A NAC must deliver 2.5 A at 400 ft one way, and the allowed drop is 3.4 V. Which is the smallest solid copper conductor that works? (12 AWG = 1.93, 10 AWG = 1.21 ohms per 1000 ft)
- 3054Why does treating the whole NAC load as if it were at the last appliance give a conservative voltage drop result?
- 3055A 25 V speaker circuit serves 32 speakers tapped at 1 W and 8 speakers tapped at 2 W. What total power does the amplifier need to supply?
- 3056Average ambient sound in an office is 60 dBA. A horn produces 90 dBA at 10 ft. In public mode, would a person 80 ft away (free field) meet the required level?
- 3057Why should ambient sound levels be measured during the site survey of an existing building?
- 3058Corridor horns must awaken occupants in hotel rooms behind closed doors. What layout concern applies?
- 3059Which of these items is a required part of the floor plan on fire alarm shop drawings?
- 3060Why must shop drawings show ceiling heights and ceiling construction for each area?
- 3061Which documents are typically part of a fire alarm submittal package besides the drawings?
- 3062Who completes the record of completion for a new fire alarm system?
- 3063When a system is modified after acceptance, what must happen to the record documentation?
- 3064Which item on a shop drawing helps reviewers confirm the correct cable type for each area?
- 3065A design shows a notification zone layout for partial evacuation. Which information must the drawings make clear?
- 3066What is the main purpose of a fire alarm system's sequence of operation for the AHJ?
- 3067A design places a spot smoke detector 2 ft from a supply diffuser. What should the reviewer note?
- 3068A design calls for a sidewall mounted smoke detector. What placement must the drawing show?
- 3069Which standby duration does NFPA 72 require for the secondary power of an emergency voice/alarm communication system in alarm?
- 3070Which equipment locations must the shop drawings show besides initiating devices and appliances?
- 3071When should fire alarm shop drawings normally be approved by the AHJ?
- 3072A heat detector listed for 25 ft spacing is installed on an 11 ft smooth ceiling. The multiplier for that height is 0.91. What is the adjusted spacing?
- 3073A heat detector listed for 50 ft spacing is planned for a 30 ft ceiling. The multiplier is 0.34. What spacing applies?
- 3074A 20 ft wide room uses spot smoke detectors with S = 30 ft. Every point must be within 21 ft of a detector. With one row down the center, what is the maximum spacing along the row?
- 3075A speaker set on its 1 W tap produces 84 dBA at 10 ft. What level is expected at 10 ft on the 2 W tap?
- 3076An SLC is limited by the manufacturer to 40 ohms of total loop resistance. Using 18 AWG solid (7.77 ohms per 1000 ft), what is the maximum one way distance for a Class B run to the farthest device?
- 3077Within what time must the battery charger be able to recharge fully discharged secondary batteries?
- 3078Where must a smoke detector in an elevator lobby be placed in relation to the elevator doors?
- 3079A design adds new detectors to an existing panel from a different manufacturer. What must the designer confirm?
- 3080Which documents must be provided to the owner at the completion of a new system?
- 3081A system uses a digital alarm communicator transmitter (DACT). What does NFPA 72 require for its transmission means?
- 3082Under the IBC, where is a two way communication system generally required for accessible means of egress in a multistory building?
- 3083What must be stated on a shop drawing title block?
- 3084Which item should a designer include so the AHJ can see how the system responds to a waterflow signal on floor 3?
- 3085A building has a 30 ft wide by 120 ft long room with a smooth 12 ft ceiling. Spot smoke detectors use S = 30 ft. How many are needed in a single row down the center?
- 3086On a shop drawing, what does the symbol legend do?
- 3087Why must shop drawings show the location of the building's sprinkler riser and control valves?
- 3088A designer must produce battery calculations. Which current values should be used for each device?
- 3089A design places two smoke detectors 28 ft apart in a room with a smooth 10 ft ceiling. Each is 10 ft from the side walls. Does this meet the 30 ft spacing rule?
- 3090Why should notification appliance circuits be designed with some spare capacity?