Question 2012 of 297 · NICET Fire Alarm Systems Level III
How often must audible and visible notification appliances be functionally tested?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2012
- B: Annually
Explanation
Notification appliances are tested annually to verify they operate. Sound pressure levels are measured during acceptance and reacceptance testing, and again when changes in the space could affect audibility.
More questions: Maintenance
- 2013During routine annual testing of an unchanged building, must a technician take sound pressure level readings at every audible appliance?
- 2014A load voltage test shows the fire alarm battery voltage under load falls below the battery manufacturer's minimum. What is the correct action?
- 2015How often must the emergency control functions of a fire alarm system, such as elevator recall and fan shutdown, be tested?
- 2016Which party is responsible for the inspection, testing, and maintenance of a building fire alarm system?
- 2017A property manager wants to hand over ITM responsibility to your company. What does NFPA 72 require for that delegation?
- 2018Which description best defines an emergency impairment?