Question 2011 of 297 · NICET Fire Alarm Systems Level III

Under NFPA 25, how often must sprinkler control valve supervisory switches be tested?

Exactly one answer is correct.

Show solution

Correct answer to question 2011

  • D: Semiannually

Explanation

NFPA 25 requires valve supervisory switches to be tested semiannually, so a fire alarm ITM contract often visits twice a year to cover both waterflow and tamper tests. The switch must signal within two revolutions of the handwheel or one-fifth of stem travel.