Question 2014 of 297 · NICET Fire Alarm Systems Level III
A load voltage test shows the fire alarm battery voltage under load falls below the battery manufacturer's minimum. What is the correct action?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2014
- D: Replace the battery
Explanation
Batteries that fail the manufacturer's load voltage or capacity criteria must be replaced. Raising the charger voltage overcharges cells and shortens life, and running without a battery leaves the system with no secondary power.