A water leak damages a notification appliance circuit at 2 a.m. and the night guard calls your service line. What is the correct order of priorities?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2019
- C: Confirm interim measures and notifications, repair, then retest the affected portion and restore
Explanation
An emergency impairment needs prompt notification of the owner, the supervising station, and the AHJ as required, and interim measures such as a fire watch. After repair, the restored part of the system must be tested before the impairment is closed out.
More questions: Maintenance
- 2020What must happen before an impaired system is returned to service?
- 2021A student pulls a manual fire alarm box as a prank. How does NFPA 72 classify this alarm?
- 2022A dirty smoke detector that has not been cleaned in years goes into alarm with no fire. How does NFPA 72 classify this?
- 2023A maintenance worker sets off a detector with welding smoke while working without a hot work permit. How is this unwanted alarm classified?
- 2024Under NFPA 72, what does a semiannual test frequency mean in terms of allowed scheduling window?
- 2025A technician performed the previous annual test in March. Using the NFPA 72 definition of annual, which next test date still complies?