What must happen before an impaired system is returned to service?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2020
- A: The repaired part is tested, and everyone notified of the impairment is told it is restored
Explanation
Restoration includes testing the affected portion to confirm it works and notifying everyone who was informed of the impairment. Only then is the interim measure, such as a fire watch, ended.
More questions: Maintenance
- 2021A student pulls a manual fire alarm box as a prank. How does NFPA 72 classify this alarm?
- 2022A dirty smoke detector that has not been cleaned in years goes into alarm with no fire. How does NFPA 72 classify this?
- 2023A maintenance worker sets off a detector with welding smoke while working without a hot work permit. How is this unwanted alarm classified?
- 2024Under NFPA 72, what does a semiannual test frequency mean in terms of allowed scheduling window?
- 2025A technician performed the previous annual test in March. Using the NFPA 72 definition of annual, which next test date still complies?
- 2026How long must inspection, testing, and maintenance records be retained under NFPA 72?