Question 2041 of 297 · NICET Fire Alarm Systems Level III
An addressable smoke detector reports a maintenance alert because its drift compensation has reached its limit. What is the correct response?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2041
- A: Clean or replace the detector soon, since it can no longer compensate for contamination
Explanation
Drift compensation adjusts for slow contamination, and a maintenance alert means the adjustment range is used up. If not cleaned or replaced, the detector is likely to produce nuisance alarms or lose its listed sensitivity.
More questions: Maintenance
- 2042Which personnel does NFPA 72 recognize as qualified to perform inspection, testing, and maintenance of fire alarm systems?
- 2043Before the annual visit at a central station monitored building, what should the technician confirm with the central station operator?
- 2044Annual testing reveals that a beam smoke detector alarms at the correct attenuation filter, but its alignment is off and it reports trouble every few days. What is the right action?
- 2045Which description fits a central station service under NFPA 72?
- 2046A university monitors all of its buildings from a supervising station that it owns and staffs itself. What type of supervising station is this?
- 2047Under what circumstance is a remote supervising station system used?