Question 2040 of 297 · NICET Fire Alarm Systems Level III
During annual testing of an air-sampling smoke detection system, what transport time requirement applies to the farthest sampling port?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2040
- A: Smoke must reach the detector in no more than 120 seconds
Explanation
Air-sampling systems must deliver a sample from the most remote port to the detector within 120 seconds. Testing from the end of each pipe run and comparing with the acceptance baseline reveals blocked or leaking pipes.