A new tenant hung a large banner that blocks the view of a strobe in an open area. What should the inspection report say?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2062
- B: Deficiency, because the appliance is obstructed
Explanation
Visible appliances are laid out so their light reaches the whole area; an obstruction can leave occupants without a visible signal. The owner must remove the obstruction or the layout must be revised.