Question 2066 of 297 · NICET Fire Alarm Systems Level III
A building uses positive alarm sequence. After an automatic detector alarms, how long does staff have to acknowledge the signal before general alarm?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2066
- B: 15 seconds
Explanation
Under positive alarm sequence, trained staff must acknowledge the alarm within 15 seconds; then they have up to 180 seconds to investigate and reset if there is no fire. If either step fails, or a second device operates, the general alarm sounds.
More questions: Maintenance
- 2067Under positive alarm sequence, after acknowledgment, how much investigation time is allowed before the general alarm must sound?
- 2068To which type of initiating device may the alarm verification feature be applied?
- 2069The panel shows a trouble signal that the building engineer silenced yesterday. The fault has not been repaired. What should the control unit do?
- 2070Notification appliances have been silenced after an alarm on the first floor. A detector on the fourth floor then goes into alarm. What must happen?
- 2071Which signal type indicates an off-normal condition of a fire suppression system, such as a closed control valve or low air pressure?
- 2072A sprinkler contractor will close a control valve to repair a branch line. From the fire alarm perspective, how should this be managed?