To which type of initiating device may the alarm verification feature be applied?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2068
- D: Smoke detectors
Explanation
Alarm verification is a smoke detector feature that briefly delays and confirms an alarm to reduce unwanted alarms. It must not be applied to manual boxes, waterflow switches, or heat detectors, which indicate fire or flow directly.