A wall mounted strobe will cover a single 40 x 40 ft room and is centered on one wall. What minimum effective intensity is required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3027
- C: 60 cd
Explanation
For a single wall mounted appliance in a room this size, 60 cd is the minimum. Smaller rooms need less, for example 15 cd for 20 x 20 ft, and larger rooms need higher ratings or more appliances.